I got an ETek multimeter and every outlet in my home tests about 6.4V. Is that possible? I got it long ago so I can't return it, but before I go spend 50$ on a new one I figured I'd ask if that's possible appliances seem to work fine but when my catchment pump or fridge or hair dryer go on the house lights dim? Is it possible the 6V is real or do I have a bad multimeter?
-
Are you sure you're configured to test Volts?
Sounds more like Amps.
Can you post the model of the ETek? Maybe a pic of the meter?
-
Open it* up and check the fuses. It could be reading that slight AC voltage "through" the burnt-out fuse's very slight capacitance between the ends of the melted fuse.
One of the problems with modern high-impedance (high sensitivity) meters is that they will give readings if there are two electrons running around loose in the room.
Proof: set a working electronic meter on a low voltage scale and wave one of the probes around. Unless it's very humid, you will read the slight variable static voltages developed by the probe point's passage through the air.
There are times when an old-fashioned low sensitivity meter with a coil and a magnet (D'Arsonval style) will give more realistic readings than an electronic meter because they load down the circuit a little.
Another time they get flaky is when their sampling rate heterodynes with a signal near that sampling rate (or near one of its harmonics).
Terry, 230RN
* (edited to add) Meaning the meter. All of them have protective fuses inside. If the fuse is burned out, instead of passing the full measurement current through the fuse element, it will pass a certain small amount of current because the two ends of the burned-out fuse element will act as a tiny capacitor and the meter will show a small voltage because of this.
-
.
-
I got an ETek multimeter and every outlet in my home tests about 6.4V. Is that possible? I got it long ago so I can't return it, but before I go spend 50$ on a new one I figured I'd ask if that's possible appliances seem to work fine but when my catchment pump or fridge or hair dryer go on the house lights dim? Is it possible the 6V is real or do I have a bad multimeter?
Are you measuring A/C or D/C volts? It does not seem correct that every plug properly powers your stuff but only measures 6.4 volts. Throw away the multmeter.
If everything in your house plugs in and works fine then you have the proper voltage ~ 120 VAC. The house lights will dim ( I assume that you have an older house 30 years plus) when a high powered appliance like the ones you mention is turned on because the main feeder (size of the electrical wires from the pole to your house) is not sufficient to power all these appliances. I had this same problem with our old house when my air compressor was turned on.
I would contact a licensed electrician, like the one suggested by new guy, if you want to up the feeder to your house. I believe that HECO will install the feeder for free, but you need the electrician to modernize your electrical panels and house wiring = big bucks.
Or live with the temporary dimming of your house lights. Unless, your house is old enough that the wiring (hot and neutral, the two conductors) are separate and installed on ceramic posts. If this is the case, then I would strongly suggest you have your house wiring modernized to avoid problems due to the old wiring and power demands of all your modern appliances.
-
Dang bro. Sorry to hear about your troubles. Hope you don't have to rewire the house, but then that's better then having it burn down.
-
i am a journeyman electrician. if your appliances and things like that are all working it seems as tho your multimeter is junk. im not sure what fuses the guy above is talking about but if you want to have a professional come out and trouble shoot the issues you may have feel free to PM me. good luck brother
-
Are you sure you're configured to test Volts?
Sounds more like Amps.
Can you post the model of the ETek? Maybe a pic of the meter?
Yeah. Was on volts.
-
Open it up and check the fuses. It could be reading that slight AC voltage "through" the burnt-out fuse's very slight capacitance between the ends of the melted fuse.
One of the problems with modern high-impedance (high sensitivity) meters is that they will give readings if there are two electrons running around loose in the room.
Proof: set a working electronic meter on a low voltage scale and wave one of the probes around. Unless it's very humid, you will read the slight variable static voltages developed by the probe point's passage through the air.
There are times when an old-fashioned low sensitivity meter with a coil and a magnet (D'Arsonval style) will give more realistic readings than an electronic meter because they load down the circuit a little.
Another time they get flaky is when their sampling rate heterodynes with a signal near that sampling rate (or near one of its harmonics).
Terry, 230RN
crap. That makes a lot of sense. Sounds like you know your shit. I also notice it reads a tenth or so volts when I break the circuit. Not sure if that's consistent with what you said. I got called into work all day so when I get home tomorrow morning in gonna take out the fuse and look at it. Thanks!!
-
@ 230RN - Holy crap, Terry... I lost you at, "Open it up and check the fuses." ;D
@ Buttnutt - Satoru Oshiro from SOS Electric was super on-it with getting rid of our old knob and tube, and bringing our house into compliance with current code.
He's a smaller, older Japanese dude who still seems spry enough to climb around tight crawlspaces, and he is old-school (won't rip you, but isn't afraid to tell you like it is).
Just my personal experience. :shaka:
Thanks man. That's actually awesome cause he sounds just like what I've been looking for. Most electricians I meet or call to consult are very short and abrupt and won't help me out with little projects, but small as they are, I just can't do all things on my own. I know they wanna make big bucks and they're not into charity cases but jeez. I'm gonna look that guy up when I need someone. Thanks!
-
Are you measuring A/C or D/C volts? It does not seem correct that every plug properly powers your stuff but only measures 6.4 volts. Throw away the multmeter.
If everything in your house plugs in and works fine then you have the proper voltage ~ 120 VAC. The house lights will dim ( I assume that you have an older house 30 years plus) when a high powered appliance like the ones you mention is turned on because the main feeder (size of the electrical wires from the pole to your house) is not sufficient to power all these appliances. I had this same problem with our old house when my air compressor was turned on.
I would contact a licensed electrician, like the one suggested by new guy, if you want to up the feeder to your house. I believe that HECO will install the feeder for free, but you need the electrician to modernize your electrical panels and house wiring = big bucks.
Or live with the temporary dimming of your house lights. Unless, your house is old enough that the wiring (hot and neutral, the two conductors) are separate and installed on ceramic posts. If this is the case, then I would strongly suggest you have your house wiring modernized to avoid problems due to the old wiring and power demands of all your modern appliances.
Yeah. I confirmed I'm measuring AC volts and setting the multimeter to 200V range as its the closest to 120. But funny thing is, the house is built 2008 and i bought it three yrs ago, but I tell you, the more I do home projects the more I see the builder cut some serious corners on all sorts of shit. Specially the electric. Outdoor security lights stopped workin one by one. sunken in 15 amp duplex on a 20 amp breaker. Which just stopped Workibg! Serious first time buyer learning lesson for me. K. Back to topic.
But the feeder enters the ground down a pole about 200' from the house and after that is the breaker box. So I'd need a back ho to dig up that line. and i aint rich! But is guess its the thicker more modern line you're talking about, but with this builder.....I wouldn't be surprised if its as thin as indoor guage wire :0
I gotta check that multimeter. No way my fridge compressor n catchment pump could be going on/off with such low voltage.
Mahalo!!
-
Dang bro. Sorry to hear about your troubles. Hope you don't have to rewire the house, but then that's better then having it burn down.
yeah man. I'm really getting scared of the wiring in this place!
-
i am a journeyman electrician. if your appliances and things like that are all working it seems as tho your multimeter is junk. im not sure what fuses the guy above is talking about but if you want to have a professional come out and trouble shoot the issues you may have feel free to PM me. good luck brother
i think he's talkin bout the fuse in the multimeter. The manual says it has one. So I'm gonna check on that tomorrow. But I'll see what happens and PM you if I don't figure this out. Thanks!
-
Oh, sorry. I should have specified the fuses in the meter more clearly. My bad. Will edit the original post.
The rest of the stuff is my normal discussion on certain measuring problems with high-impedance (high sensitivity) electronic meters. Optional reading. Basically, sometimes their hyper-sensitivity and their measuring (sampling) frequencies lead to bad readings.
I have a wide assortment of electronic meters, and they have their place, but actually, I usually use one of several D'Arsonval (magnet-and-coil) meters. My favorite is a little Radio Shack 2000 ohms-per-volt one that cost about ten bucks many years ago.
When that one says ten volts, there's really ten whole honest-to-gawd manly hairy-assed volts present, and not pansy little artifacts due to static or stray magnetic fields. :D
Terry, 230RN
REF (D'Arsonval moving-coil meter movement):
http://www.engineersedge.com/instrumentation/electrical_meters_measurement/images/darsonval.gif (http://www.engineersedge.com/instrumentation/electrical_meters_measurement/images/darsonval.gif)
-
The best electrical meter that you can buy is the Fluke T5-600. I am a licensed journeyman electrician and i have never once seen a fellow electrician use anything bought from radio shack. Did you say the house was built in 2008? If that is the case it is highly unlikely that you would need a service upgrade. You are likely to have a 125 amp service which is plenty for an average sized house. Imaginre that 50% of the houses on this island have 75 amp services. The lights dimming when you plug in devices with a very heavy draw is a sign that specific circuits may be overloaded, buut doesnt necessarily mean that you have to change the feed from heco. Also, if you have an underground service it can be extremely costly to do a service ugrade because it often requires digging up the trench and rerunning a bigger conduit to support the bigger wire required for the service upgrade. If you get yourself a good tester, take the panel cover off of yourr loadcenter and test each breaker for voltage. place one lead of the tester on the ground buss bar and then touch the fastening screw where the wire enters each breaker. if you do not get 120, or something very close to that, on each breaker, then you may have a bad breaker.
-
+1 to what kanakamaoli23 said.
I have a Fluke 77 that is almost 20 years old and it still works like a champ!
Be very careful if you remove the load center (electrical circuit breaker panel) cover to measure the voltage as the main buss bars will be exposed. It is most likely that as kanakamaoli23 stated that the particular circuit is overloaded, but not quite enough to pop the breaker. Possible, but highly unlikely, is that the contractor installed wiring that is not sufficient and does not meet electrical code - minimum 14 gauge for a 15 amp circuit.
Your fridge should be plugged into a dedicated circuit - check the labels in the electrical panel. You most likely need to have some of the plugs split into separate circuits. You can have mini-breakers (breakers that take 1/2 the physical space of a standard breaker) installed if there are no spare/open slots in the electrical panel.
Even the bathroom plugs should be a separate circuit from your other plugs in the house - with GFI plugs. The contractor may have cut corners by combining the circuits for the plugs instead of home running separate circuits to save a couple of bucks. I.e., the bedroom plugs, bathroom plugs, living room plugs, and kitchen plugs should all have their own circuit/breaker.
I am not an electrician, but have counted wires . . .
-
The feeder off the pole should be fine. If it is undersized, then the contractor should be liable for the cost for ugrading the feeder. I have not researched it, but it most likely does not meet the building code requirements if is not sized at least at what kanakamaoli23 stated - 125A.
-
When that one says ten volts, there's really ten whole honest-to-gawd manly hairy-assed volts present, and not pansy little artifacts..........
Yo man, if anyone knows that dude on 2ahawaii that is compiling a list of the best quotes from post on all the forums send'm this one; cuz its GOT to go on the list :rofl: F'ing classic man!
So I pulled out the fuse and its fried. I don't even see the filament. Like its vaporized. I think someone tested some high amps with this thing, toasted it, and returned it. Thanks for the link. I'm gonna go into town to get a fuse and I'll see about a spare meter if they got that old one you mentioned. If the fuse don't fix it, I'd guess the meter was fried all together. Then I'll check out your link for sure.
-
The best electrical meter that you can buy is the Fluke T5-600. I am a licensed journeyman electrician and i have never once seen a fellow electrician use anything bought from radio shack. Did you say the house was built in 2008? If that is the case it is highly unlikely that you would need a service upgrade. You are likely to have a 125 amp service which is plenty for an average sized house. Imaginre that 50% of the houses on this island have 75 amp services. The lights dimming when you plug in devices with a very heavy draw is a sign that specific circuits may be overloaded, buut doesnt necessarily mean that you have to change the feed from heco. Also, if you have an underground service it can be extremely costly to do a service ugrade because it often requires digging up the trench and rerunning a bigger conduit to support the bigger wire required for the service upgrade. If you get yourself a good tester, take the panel cover off of yourr loadcenter and test each breaker for voltage. place one lead of the tester on the ground buss bar and then touch the fastening screw where the wire enters each breaker. if you do not get 120, or something very close to that, on each breaker, then you may have a bad breaker.
Thanks for the tip on that meter model. And yeah, I was thinking bout a bad breaker so I looked on YouTube and found a guide for testing the breaker. So thanks for that tip. Do you know how I can tell if I have 125 amp service? Is it stamped anywhere? Any way to tell?
-
If I'm not mistaken, that's usually universal household rating. According to codes and whatnot. 125.
-
+1 to what kanakamaoli23 said.
I have a Fluke 77 that is almost 20 years old and it still works like a champ!
Be very careful if you remove the load center (electrical circuit breaker panel) cover to measure the voltage as the main buss bars will be exposed. It is most likely that as kanakamaoli23 stated that the particular circuit is overloaded, but not quite enough to pop the breaker. Possible, but highly unlikely, is that the contractor installed wiring that is not sufficient and does not meet electrical code - minimum 14 gauge for a 15 amp circuit.
Your fridge should be plugged into a dedicated circuit - check the labels in the electrical panel. You most likely need to have some of the plugs split into separate circuits. You can have mini-breakers (breakers that take 1/2 the physical space of a standard breaker) installed if there are no spare/open slots in the electrical panel.
Even the bathroom plugs should be a separate circuit from your other plugs in the house - with GFI plugs. The contractor may have cut corners by combining the circuits for the plugs instead of home running separate circuits to save a couple of bucks. I.e., the bedroom plugs, bathroom plugs, living room plugs, and kitchen plugs should all have their own circuit/breaker.
I am not an electrician, but have counted wires . . .
Allright, so the fridge, water pump, and bathroom plugs I use the hair dryer on, are all on their own breakers - and the house lights dim when I use them. Can anyone explain that? Shouldn't dim if they're on their own breaker unless like someone said, the feeder is insufficient right? I mean could be a bad breaker but THREE bad breakers for those three circuits??
-
The feeder off the pole should be fine. If it is undersized, then the contractor should be liable for the cost for ugrading the feeder. I have not researched it, but it most likely does not meet the building code requirements if is not sized at least at what kanakamaoli23 stated - 125A.
any way of telling if its 125a?
-
.........wiring that is not sufficient and does not meet electrical code - minimum 14 gauge for a 15 amp circuit.....
how do I tell what guage I got installed. All wires are that standard black and white looking stuff. Guage looks like what I've seen everywhere. Not thick or thin. Any way to tell?
-
Allright, so the fridge, water pump, and bathroom plugs I use the hair dryer on, are all on their own breakers - and the house lights dim when I use them. Can anyone explain that? Shouldn't dim if they're on their own breaker unless like someone said, the feeder is insufficient right? I mean could be a bad breaker but THREE bad breakers for those three circuits??
Highly unlikely, but still possible to have 3 defective breakers. Best to check to be sure. Seen it (unlike things happen) more often than I would think.
Not sure how to tell gauge of feeder by looking? Kanakamaoli23?
The symptom you describe points more to an undersized (or damaged) feeder. I would suggest calling HECO to inquire about the feeder size & describe what you are experiencing. I seriously doubt that HECO would provide a sub-standard feeder, but I have learned never to assume anything. If anything, try to have them schedule a technician to check it to make sure.
Don't stress too much about the dimming lights as it is only for a few minutes. Right? I don't think you are running the hair dryer for hours.
-
The meter main outside will have the rating on the inside of the cover. Normally the label will say 125a max load but the size of the breaker inside will be 100a breaker.
-
Thanks kanakamaoli23 and wirecounter! I'll get the fuse for the meter and once it's working, or I get a new one, ill check out the panel.
Big mahalos!
-
The wire from Heco is likely not the culprit. Heco will pull in the proper size wire depending on the size of the service the home owner chooses. Maybe the contractor ran a smaller than adequate cable from the meter main to the load center inside the home. If you have a 100a main breaker outside, the wire between the panel outside and the panel inside the house should read #2 on it.
-
I really don't understand what the fuse is that you are referring to that was fried. Are you referring to a breaker? Houses don't have fuses like the way a car would.
-
I really don't understand what the fuse is that you are referring to that was fried. Are you referring to a breaker? Houses don't have fuses like the way a car would.
He talking about a fuse in his multi meter.
-
Ahhhh. That makes sense. Lol. I thought he was referring to something he found in his house.
-
Ps I do work trade for firearms. ;) :thumbsup:
-
The wire from Heco is likely not the culprit. Heco will pull in the proper size wire depending on the size of the service the home owner chooses. Maybe the contractor ran a smaller than adequate cable from the meter main to the load center inside the home. If you have a 100a main breaker outside, the wire between the panel outside and the panel inside the house should read #2 on it.
yeah......you heard already. The fuse in the meter. So anyway, thanks, but I don't know how I can see the wire from outside the house to the breaker panel. Maybe when I take off the cover to the panel I can tell. Is that the way you think I could see the wire? Cause from the meter outside the wire goes underground but even from the meter to the ground I can't see any wire.
-
Yes you must remove the cover on the panel to see the size of the wiring.
-
The wire from Heco is likely not the culprit. Heco will pull in the proper size wire depending on the size of the service the home owner chooses. Maybe the contractor ran a smaller than adequate cable from the meter main to the load center inside the home. If you have a 100a main breaker outside, the wire between the panel outside and the panel inside the house should read #2 on it.
Never thought of that, what you say makes sense. More likely, this cable rather than the HECO feed.
So, I would suggest:
1) check the breakers. If okay, then
2) Check the cable marker whlie you have the panel cover off. If okay, then
3) Contact HECO.
Good luck BN! Let us know what you discover.
-
Thanks everyone. I'm going to get a fuse now. Letter today or tomorrow I'll see what the voltage reading at the outlets are after replacing it. Then I'll go from there with taking the panel cover off or not. Fingers crossed!
-
OP- Perhaps I missed something not reading word for word, but what is the actual problem you are having in the first place?
I would not be assuming you need to have a new feed wire pulled or anything of that sort just yet, and also I would highly caution against taking the cover off of your electrical panel also just yet because it does not sound like you know what you are doing (no offense) and there are plenty of things you can accidentally touch in there that can KILL YOU
Most multimeters take a special fuse, not just something you pick up at home depot. When it says replace only with such and such a fuse please heed that warning. I can tell you from experience. I was doing a startup at a water remediation plant, inside of the main pump station panel we had built which is supplied by 3 phase 480v 200amp serivice. I was testing all sorts of items and had not remembered my meter leads were still set for measuring current when I was testing 4-20ma devices... Most good meters will beep at you when you turn the knob to voltage and the leads are not connected properly.. this one did not... well.. I went to take a voltage measurement on one of the pump station breakers and in an instant there was a good few sparks, and a gunshot sound that was my multimeter literally exploding. It was a good thing I was not holding the meter. Also good that I had a spare meter with me. A while back I had replaced a blown fuse in it with a generic one, not the 10 dollar fluke one... Lesson learned.
Also, when you do take voltage measurements, Measure from hot to neutral (hot is the smaller blade) this should read around 120v
Measure from hot to ground. also should read around 120v
Measure from neutral to ground. should read 0v or close to thereabouts.
If your meter has a recording function you can turn that on and see how much voltage sag you are getting when heavy loads are turned on if that is the problem you are having.
-
OP- Perhaps I missed something not reading word for word, but what is the actual problem you are having in the first place?
I would not be assuming you need to have a new feed wire pulled or anything of that sort just yet, and also I would highly caution against taking the cover off of your electrical panel also just yet because it does not sound like you know what you are doing (no offense) and there are plenty of things you can accidentally touch in there that can KILL YOU
Most multimeters take a special fuse, not just something you pick up at home depot. When it says replace only with such and such a fuse please heed that warning. I can tell you from experience. I was doing a startup at a water remediation plant, inside of the main pump station panel we had built which is supplied by 3 phase 480v 200amp serivice. I was testing all sorts of items and had not remembered my meter leads were still set for measuring current when I was testing 4-20ma devices... Most good meters will beep at you when you turn the knob to voltage and the leads are not connected properly.. this one did not... well.. I went to take a voltage measurement on one of the pump station breakers and in an instant there was a good few sparks, and a gunshot sound that was my multimeter literally exploding. It was a good thing I was not holding the meter. Also good that I had a spare meter with me. A while back I had replaced a blown fuse in it with a generic one, not the 10 dollar fluke one... Lesson learned.
Also, when you do take voltage measurements, Measure from hot to neutral (hot is the smaller blade) this should read around 120v
Measure from hot to ground. also should read around 120v
Measure from neutral to ground. should read 0v or close to thereabouts.
If your meter has a recording function you can turn that on and see how much voltage sag you are getting when heavy loads are turned on if that is the problem you are having.
Problem started here. So it kinda turned into a issue of his meter is blown or house wiring sucks.
I got an ETek multimeter and every outlet in my home tests about 6.4V. Is that possible? I got it long ago so I can't return it, but before I go spend 50$ on a new one I figured I'd ask if that's possible appliances seem to work fine but when my catchment pump or fridge or hair dryer go on the house lights dim? Is it possible the 6V is real or do I have a bad multimeter?
-
Yeah, I did see that part but obviously something caused him to check the voltage in the first place. Clearly the actual voltage is not 6.4vac as nothing will run from that. It is however possible to measure such a voltage if the breakers were all turned off when he was taking these readings as there will be some voltage potential between ground and the de-energized circuit.
OP- If the problem is the lights dimming, are they just dimming for a second or it is a constant thing?
All of those loads you listed will present a heavy current draw and even in a modern house with sufficient wiring you will likely still see dimming especially when they are initially turned on. You should not really notice a significant and constant dimming of your house lights the entire time though.
-
OP- Perhaps I missed something not reading word for word, but what is the actual problem you are having in the first place?
I would not be assuming you need to have a new feed wire pulled or anything of that sort just yet, and also I would highly caution against taking the cover off of your electrical panel also just yet because it does not sound like you know what you are doing (no offense) and there are plenty of things you can accidentally touch in there that can KILL YOU
Most multimeters take a special fuse, not just something you pick up at home depot. When it says replace only with such and such a fuse please heed that warning. I can tell you from experience. I was doing a startup at a water remediation plant, inside of the main pump station panel we had built which is supplied by 3 phase 480v 200amp serivice. I was testing all sorts of items and had not remembered my meter leads were still set for measuring current when I was testing 4-20ma devices... Most good meters will beep at you when you turn the knob to voltage and the leads are not connected properly.. this one did not... well.. I went to take a voltage measurement on one of the pump station breakers and in an instant there was a good few sparks, and a gunshot sound that was my multimeter literally exploding. It was a good thing I was not holding the meter. Also good that I had a spare meter with me. A while back I had replaced a blown fuse in it with a generic one, not the 10 dollar fluke one... Lesson learned.
Also, when you do take voltage measurements, Measure from hot to neutral (hot is the smaller blade) this should read around 120v
Measure from hot to ground. also should read around 120v
Measure from neutral to ground. should read 0v or close to thereabouts.
If your meter has a recording function you can turn that on and see how much voltage sag you are getting when heavy loads are turned on if that is the problem you are having.
Hey thanks for the warnings and advice. Funny thing is that this post makes me seem like a total noob but I've replaced a 50A breaker for my range, replaced the thermostat and elements in my water heater, and installed lighting in my kitchen and bathroom, so im not totally green, but know my limits and when to call a professional. Thing is when i did all that, it was during the first year here and i was using my friends multimeter before he moved. so the multimeter I originally bought sat in my tool bag and never got used till now. So anyways, the next poster after you postulated a logical assumption which was that something must have started this whole thing, and that is true. I just got home with the fuse so ill post in a few minutes what I get and I'll give the history as well, cause that will probably help you guys help me.
-
Btw thanks to RN230 for tactfully PM'ing and figuring out I must have blown the fuse in the multi by using it incorrectly :0
-
K guys. Now I'm confused, unless someone can figure this out for me.
Here's what started this all: next to my sink I have a GFI duplex outlet with a green indicator LED in the upper right, on a 20A breaker; the finishing plate is cracked beneath it, the lower left of the outlet is sunken in, and there's char in the lower left T-slot; it always worked fine, tested monthly.
i only have a microwave plugged into it when I'm home; when I go out I unplug it (cause the outlet looks funny) A week ago I plugged in the mic and I heard a slight pop and think I saw a spark, but the GFCI and breaker didn't trip. The mic wasn't working but the outlet LED was still on. I pressed the test button and reset it a few times and the LED would still come on but the mic didn't work.
A couple of days ago I got the time to test the non-GFCI outlet on the counter upstream of it on the same breaker. It worked ok. When I incorrectly used my multimeter on THAT outlet it blew the multimeter fuse. but I not knowing this, kept testing it, and the rest of the house, and getting the ~6V readings, but when testing the aforementioned GFCI outlet, I would get 0.1V (almost zero), which made since since the mic wouldn't work.
Ok, now the confusing part: I just replaced the multimeter fuse and tested the outlet upstream from the GFCI outlet and it was reading 114V. THEN, I reset the GFCI outlet that wasn't working a few days ago, and it said around 114V as well??? Then I plugged in the mic and it worked??? I took a piss and got a drink and tested both outlets again ten min later and they both read around 118V?
So here we go gentlemen; is there an explanation for the following:
1) how could the GFCI outlet pop and spark but not trip the GFCI mechanism or the breaker?
2) how could the mic not have worked in the outlet, but the GFCI outlet indicator LED was still on?
3) how could the mic in the outlet have NOT been working after the pop/spark, and then suddenly BE working four days later?
4) why would the two outlets that are the only outlets on the 20A breaker, with nothing plugged into them, read 114V and then 118V ten min later?
5) if the answer to "4" above is because other things in the house going on/off causes the flux, does it indicate I still have a problem with the feeder, breaker, or anything else in the system?
I went into the detail so you guys would still help me and not blow me off, thinking I'm a dope who sent you on a wild goose chase since the initial question was related to me blowing the fuse in the multi meter. So if you could answer the questions above, that would be awesome, cause I'm still not in the clear on this issue.
Big mahalos !!! Seriously!
-
K guys. Now I'm confused, unless someone can figure this out for me.
Here's what started this all: next to my sink I have a GFI duplex outlet with a green indicator LED in the upper right, on a 20A breaker; the finishing plate is cracked beneath it, the lower left of the outlet is sunken in, and there's char in the lower left T-slot; it always worked fine, tested monthly.
i only have a microwave plugged into it when I'm home; when I go out I unplug it (cause the outlet looks funny) A week ago I plugged in the mic and I heard a slight pop and think I saw a spark, but the GFCI and breaker didn't trip. The mic wasn't working but the outlet LED was still on. I pressed the test button and reset it a few times and the LED would still come on but the mic didn't work.
A couple of days ago I got the time to test the non-GFCI outlet on the counter upstream of it on the same breaker. It worked ok. When I incorrectly used my multimeter on THAT outlet it blew the multimeter fuse. but I not knowing this, kept testing it, and the rest of the house, and getting the ~6V readings, but when testing the aforementioned GFCI outlet, I would get 0.1V (almost zero), which made since since the mic wouldn't work.
Ok, now the confusing part: I just replaced the multimeter fuse and tested the outlet upstream from the GFCI outlet and it was reading 114V. THEN, I reset the GFCI outlet that wasn't working a few days ago, and it said around 114V as well??? Then I plugged in the mic and it worked??? I took a piss and got a drink and tested both outlets again ten min later and they both read around 118V?
So here we go gentlemen; is there an explanation for the following:
1) how could the GFCI outlet pop and spark but not trip the GFCI mechanism or the breaker?
2) how could the mic not have worked in the outlet, but the GFCI outlet indicator LED was still on?
3) how could the mic in the outlet have NOT been working after the pop/spark, and then suddenly BE working four days later?
4) why would the two outlets that are the only outlets on the 20A breaker, with nothing plugged into them, read 114V and then 118V ten min later?
5) if the answer to "4" above is because other things in the house going on/off causes the flux, does it indicate I still have a problem with the feeder, breaker, or anything else in the system?
I went into the detail so you guys would still help me and not blow me off, thinking I'm a dope who sent you on a wild goose chase since the initial question was related to me blowing the fuse in the multi meter. So if you could answer the questions above, that would be awesome, cause I'm still not in the clear on this issue.
Big mahalos !!! Seriously!
I will take a stab at it.
1) The mic plug in the outlet may not have made contact with the outlet, therefore, creating the pop/spark you heard/saw when you turned it on. I would recommend replacing the outlet since there is charring and it is loose. The GFI or breaker will not activate since no ground fault (short to ground from the hot terminal) nor the current draw exceeded the 15 or 20 amps on breaker.
2) No good connection in the outlet.
3) Now have good connection after unplugging then plugging.
4) Voltage will fluctuate depending on the load on the electrical grid, not necessarily within your home. That is why high end electronic equipment should be plugged in to a line conditioner (keeps the voltage clean & steady). Downtown Honolulu is notorious for having power fluctuations.
5) What about the dimming house lights when you turn on your high powered appliances? Only suggested the feeder size since you mentioned house lights dimmed when you activate your high powered appliances.
-
I will take a stab at it.
1) The mic plug in the outlet may not have made contact with the outlet, therefore, creating the pop/spark you heard/saw when you turned it on. I would recommend replacing the outlet since there is charring and it is loose. The GFI or breaker will not activate since no ground fault (short to ground from the hot terminal) nor the current draw exceeded the 15 or 20 amps on breaker.
2) No good connection in the outlet.
3) Now have good connection after unplugging then plugging.
4) Voltage will fluctuate depending on the load on the electrical grid, not necessarily within your home. That is why high end electronic equipment should be plugged in to a line conditioner (keeps the voltage clean & steady). Downtown Honolulu is notorious for having power fluctuations.
5) What about the dimming house lights when you turn on your high powered appliances? Only suggested the feeder size since you mentioned house lights dimmed when you activate your high powered appliances.
Thanks for answering the questions so clearly. When I make the time, maybe when I replace the suspect GFI outlet in the kitchen, I'll take the cover off the breaker panel,and see what size the line is coming into the box, this way I can at least rule out that being insufficient.......thanks again!
:shaka:
-
Glad I could help.
I would use a power strip instead of unplugging & plugging in the microwave. Just flip the switch.
Also, remember to turn off the breaker before working on replacing the plug.
-
Yeah man.....will do. I actually ran a power strip to the upstream outlet and tripped the test button on the sink gfi to kill it, for whatever that's worth. So ill be using the power strip with the mic until I replace that outlet.....
Mahalo hou!
-
So here we go gentlemen; is there an explanation for the following:
1) how could the GFCI outlet pop and spark but not trip the GFCI mechanism or the breaker?
2) how could the mic not have worked in the outlet, but the GFCI outlet indicator LED was still on?
3) how could the mic in the outlet have NOT been working after the pop/spark, and then suddenly BE working four days later?
4) why would the two outlets that are the only outlets on the 20A breaker, with nothing plugged into them, read 114V and then 118V ten min later?
5) if the answer to "4" above is because other things in the house going on/off causes the flux, does it indicate I still have a problem with the feeder, breaker, or anything else in the system?
1) sometimes you will get a spark and a small pop when you plug in certain items. My cordless drill battery charger does it every single time. if you are constantly plugging in and unplugging the microwave it could happen. If the contacts in the outlet are so worn they no longer have good contact pressure this will also cause arching which will lead to this char you are talking about and it will also char your plug and create little tiny weld spots. The arching that occurs when you plug something in is not a ground fault so it would not trip the outlet.
2) Are you sure the light means it is ok? some GFCI outlets only have a light on them when they are tripped... although not usually green. Anyway it could be you just did not have a good connection or something.. who knows.
3) Again maybe just not a good connection or faulty outlet. or faulty plug on your microwave with an intermittent connection.
4/5) this is pretty normal to see. Especially if you live in an area with high loads on your shared powerline and you most likely share a transformer with a few neighbors as well. Ive lived in places that would go from 110vac during the day to 120-125vac at night. It does not mean you have undersized wiring just a fact of life with an overtaxed power grid. Your meter probably has some error in it as well, cheap meters are not entirely accurate to begin with.
The way your kitchen plugs should have been wired is that the first wire from the breaker goes to the GFCI outlet which will have an input and an output, what this does is allows all the rest of the plugs to also be protected but they do not have to be GFCI outlets themselves. So then the output from the GFCI would go to the next receptacle and so on. (the other outlets would not have a true in and out they just have two screws on each side)
I would suggest just replace the GFCI outlet with a new one, paying attention to how it is wired as there is an in and out just like I mentioned.
-
+1
the in and out he is referring to will be marking by the words line and load. line will be the wire coming from the breaker and load will be the wire going to the next outlet in the chain.
-
1) sometimes you will get a spark and a small pop when you plug in certain items. My cordless drill battery charger does it every single time. if you are constantly plugging in and unplugging the microwave it could happen. If the contacts in the outlet are so worn they no longer have good contact pressure this will also cause arching which will lead to this char you are talking about and it will also char your plug and create little tiny weld spots. The arching that occurs when you plug something in is not a ground fault so it would not trip the outlet.
2) Are you sure the light means it is ok? some GFCI outlets only have a light on them when they are tripped... although not usually green. Anyway it could be you just did not have a good connection or something.. who knows.
3) Again maybe just not a good connection or faulty outlet. or faulty plug on your microwave with an intermittent connection.
4/5) this is pretty normal to see. Especially if you live in an area with high loads on your shared powerline and you most likely share a transformer with a few neighbors as well. Ive lived in places that would go from 110vac during the day to 120-125vac at night. It does not mean you have undersized wiring just a fact of life with an overtaxed power grid. Your meter probably has some error in it as well, cheap meters are not entirely accurate to begin with.
The way your kitchen plugs should have been wired is that the first wire from the breaker goes to the GFCI outlet which will have an input and an output, what this does is allows all the rest of the plugs to also be protected but they do not have to be GFCI outlets themselves. So then the output from the GFCI would go to the next receptacle and so on. (the other outlets would not have a true in and out they just have two screws on each side)
I would suggest just replace the GFCI outlet with a new one, paying attention to how it is wired as there is an in and out just like I mentioned.
Wow. Great info. Thanks!
Re: the gfi indicator light, I confirmed the light is on when the outlet is hot, and it goes off when its tripped, and it is green.
Re: the in/out wiring of the gfi and proper setup, the corner-cutter that wired the house pointlessly wired the kitchen suboptimally.
IOW, there are gfi outlets on either side of the sink, and another counter outlet on either side of the sink - further away from the sink. And both sets of outlets are on separate breakers.
But the left and right outlets furthest from the sink are NOT wired/controlled by the output of the gfi's NEXT to the sink!?!
you believe that? i mean there is cutting corners and then theres just plain laziness, and not wiring the non gfi counter outlets down stream from the gfi's is just friggin pointless and lazy cause the wood frame was bare so it would not have taken any more effort to do things ideally!
So i dont know if the distant outlet was wired first or the gfi was wired first but the output of it wasnt used to wire the distant outlet. I guess i'll see when i open up that suspect sink outlet and see if the output is being used.
So I obviously have to watch out for wet counters/floors when working with anything plugged into the two non gfi counter outlets.
Thanks for all the info man!
:shaka:
-
+1
the in and out he is referring to will be marking by the words line and load. line will be the wire coming from the breaker and load will be the wire going to the next outlet in the chain.
Ah ok. So if the there is nothing on the load marked side, then that means that outlet is the last one in the chain, right? Cause there's only two on that breaker, and the distant non gfi outlet isn't controlled by the sink gfi one.......so....I guess I just answered my own question?
-
Ah ok. So if the there is nothing on the load marked side, then that means that outlet is the last one in the chain, right? Cause there's only two on that breaker, and the distant non gfi outlet isn't controlled by the sink gfi one.......so....I guess I just answered my own question?
What you could do if the GFCI outlet is the last one in the chain, Is just put the GFI where the other outlet is located at and just switch them. This will involve taking out the outlet and removing the wires and then testing them to see which one goes where but.. at least all of your kitchen plugs would be protected.
It is not uncommon to see laziness in residential construction IMO. We are currently finishing a remodel job and in just one small bathroom I found three separate places where someone spliced the romex together with no box and just left it hanging in the wall. I shudder to think what the rest of the house is like. Some people just do not take any pride in their work. I hate the job I am doing right now but I still take pride in my work.
-
What you could do if the GFCI outlet is the last one in the chain, Is just put the GFI where the other outlet is located at and just switch them. This will involve taking out the outlet and removing the wires and then testing them to see which one goes where but.. at least all of your kitchen plugs would be protected.
It is not uncommon to see laziness in residential construction IMO. We are currently finishing a remodel job and in just one small bathroom I found three separate places where someone spliced the romex together with no box and just left it hanging in the wall. I shudder to think what the rest of the house is like. Some people just do not take any pride in their work. I hate the job I am doing right now but I still take pride in my work.
Yeah that's a good idea. I don't mind the extra time since im gonna be taking out one of the outlets anyway; plus its cheaper than buying a new gfi outlet anyways, which is the only other alternative to simply leaving it non gfi - which I don't want to do. And it is sooo true about some people not taking pride in their work. You see the result of that in all aspects of home construction. But of course they would never cut corners or go lazy if they were working on their home......so they're always conscious of doing a shit job whenever they do it - that I'm sure of.
Thanks!!
-
you could also just install a GFCI breaker for the kitchen circuits. probably a little easier and less work than swwitching the two outlet locations. if you remove the gfci and it does not have any wiring attached to the load side, that means that no other outlet is protected by that gfci
-
i have noticed that you only get electricians who cut corners if you hire unlicensed guys because the licensed ones are too expensive. a licensed individual would never leave a junction inside of a wall, without being in an enclosure because we put our license on the line every time we do a job. if you are unlicensed, you are also unliable in the event of something like a fire. moral of the story, pay the extra dime for the licensed guy and avoid a whole host of issues down the line! :shaka:
-
i have noticed that you only get electricians who cut corners if you hire unlicensed guys because the licensed ones are too expensive. a licensed individual would never leave a junction inside of a wall, without being in an enclosure because we put our license on the line every time we do a job. if you are unlicensed, you are also unliable in the event of something like a fire. moral of the story, pay the extra dime for the licensed guy and avoid a whole host of issues down the line! :shaka:
I didn't think of that. I guess it wouldn't be the licensed guys doin shit jobs. At least it would be unlikely. Well I know the contractors name who had this house built and when the building craze was peaking, he was cranking out houses a dozen ongoing at once, like he was slinging hotdogs out of a cart in Times Square!
Electric, plumbing, carpentry; all sorts of mismatched shit and what looks like factory seconds. I'd shoe this guy in da grapes if I ever met him! Hard lesson learned!
-
i have noticed that you only get electricians who cut corners if you hire unlicensed guys because the licensed ones are too expensive. a licensed individual would never leave a junction inside of a wall, without being in an enclosure because we put our license on the line every time we do a job. if you are unlicensed, you are also unliable in the event of something like a fire. moral of the story, pay the extra dime for the licensed guy and avoid a whole host of issues down the line! :shaka:
I wish that were the whole truth. Unfortunately, there are electricians who are licensed and in business 20 years that sometimes, for whatever reason, do crappy work.
I had the power in the living room just stop working. Tried to troubleshoot, and couldn't find the cause. So, I contacted my home warranty company who contacted this electrician (I'll not give the name). This guy first made me remove my ceiling paint because he wanted to cut holes in the ceiling to trace the trouble. I had to pay a HAZMAT company to test for asbestos then remove it according to federal and state safety and health regs. Apparently that 1970's blown "popcorn" ceiling stuff did have asbestos!
After all that, still can't find the electrical issue. He told the warranty company he needed to rewire the whole circuit because the ALUMINUM WIRE can't stay and be within code. Anything he fixed had to meet code, and he couldn't fix the problem without bypassing that wire and just running copper..
So, after a month waiting for approval, I called the guy, and he has basically forgotten to check with the warranty people! Called me back next day and said the work was approved.
Scheduled the repair for a Friday afternoon. He and his son, maybe 20-something, came about 12:30, and they were gone when I came home at 3:00. Basically, they patched in the power from another circuit, ran a 2-inch wide wooden conduit strip down my living room wall to hide the spliced wire, replaced an outlet in a bedroom using sub-par parts (aluminum wiring needs special parts or it's a fire hazard), and never bothered to explain why the circuit wasn't replaced! So I basically now have TWO circuits combined on ONE breaker with the neutral still running on the old breaker. He only ran a connection to the hot wire of the living room circuit!
Warranty company said if I wasn't happy they would send him out to try again, but they can't send a different person for the same job. I filed a lengthy, detailed complaint and canceled my warranty. When the salesman called to try and get me to renew again, I talked his ear off, too! I'm sure that company couldn't care less about my $350 a year.
Why this guy didn't do the work that was authorized is beyond me. He was set for making some good money, was going to fix my problem after making me wait over a month and remove my ceiling, and be a hero. Instead, I was totally pissed!
I sat down that night, traced out the problem (since I wanted to fix his work, too, so my house didn't catch fire), and I found the original reason for the power outage. The line running around the living room went under the front door threshold. It was bent at an acute angle on one side of the doorway as it came back up into the room from outside beneath the frame of the house. Over time, that bend must have heated and finally caused the wire to break. So, I replaced the wire under the doorway with copper, and it's been fine for years now!
I hate having to bring strangers into the house to fix anything. This nightmare made the felling that much worse for every other repair!
Moral of the story: even licensed and experienced professionals don't always do professional work!
-
I wish that were the whole truth. Unfortunately, there are electricians who are licensed and in business 20 years that sometimes, for whatever reason, do crappy work.
I had the power in the living room just stop working. Tried to troubleshoot, and couldn't find the cause. So, I contacted my home warranty company who contacted this electrician (I'll not give the name). This guy first made me remove my ceiling paint because he wanted to cut holes in the ceiling to trace the trouble. I had to pay a HAZMAT company to test for asbestos then remove it according to federal and state safety and health regs. Apparently that 1970's blown "popcorn" ceiling stuff did have asbestos!
After all that, still can't find the electrical issue. He told the warranty company he needed to rewire the whole circuit because the ALUMINUM WIRE can't stay and be within code. Anything he fixed had to meet code, and he couldn't fix the problem without bypassing that wire and just running copper..
So, after a month waiting for approval, I called the guy, and he has basically forgotten to check with the warranty people! Called me back next day and said the work was approved.
Scheduled the repair for a Friday afternoon. He and his son, maybe 20-something, came about 12:30, and they were gone when I came home at 3:00. Basically, they patched in the power from another circuit, ran a 2-inch wide wooden conduit strip down my living room wall to hide the spliced wire, replaced an outlet in a bedroom using sub-par parts (aluminum wiring needs special parts or it's a fire hazard), and never bothered to explain why the circuit wasn't replaced! So I basically now have TWO circuits combined on ONE breaker with the neutral still running on the old breaker. He only ran a connection to the hot wire of the living room circuit!
Warranty company said if I wasn't happy they would send him out to try again, but they can't send a different person for the same job. I filed a lengthy, detailed complaint and canceled my warranty. When the salesman called to try and get me to renew again, I talked his ear off, too! I'm sure that company couldn't care less about my $350 a year.
Why this guy didn't do the work that was authorized is beyond me. He was set for making some good money, was going to fix my problem after making me wait over a month and remove my ceiling, and be a hero. Instead, I was totally pissed!
I sat down that night, traced out the problem (since I wanted to fix his work, too, so my house didn't catch fire), and I found the original reason for the power outage. The line running around the living room went under the front door threshold. It was bent at an acute angle on one side of the doorway as it came back up into the room from outside beneath the frame of the house. Over time, that bend must have heated and finally caused the wire to break. So, I replaced the wire under the doorway with copper, and it's been fine for years now!
I hate having to bring strangers into the house to fix anything. This nightmare made the felling that much worse for every other repair!
Moral of the story: even licensed and experienced professionals don't always do professional work!
Daammmn! That's a horrible story. Did you ever call the better business bureau or the dept of consumer affairs, or whatever appropriate agency? Cause I did that a couple of times when the business left me no choice. And it sounds like your experience was worth reporting. I guess since you never know what type of service you're going to get, it's best to do jobs on your own within safety limits.
-
Daammmn! That's a horrible story. Did you ever call the better business bureau or the dept of consumer affairs, or whatever appropriate agency? Cause I did that a couple of times when the business left me no choice. And it sounds like your experience was worth reporting. I guess since you never know what type of service you're going to get, it's best to do jobs on your own within safety limits.
No reporting. My contract was with the warranty company. He was only their local contractor. I made sure they understood he was never going to enter by home again, and if the company didn't send someone else, I was canceling my service with them. It was too complicated to figure out who I should report and where. I was just out the $50 service call fee, plus the time and materials doing the job myself. My only remedy was to let the same guy back in to fix it right. I really didn't think he could be trusted at that point. Live and learn!
I'm not a bad electrician for the things I've needed. Just that one time I figured, "This power problem is taking longer to figure out than I hoped. I'll save myself some time and headaches, since Christmas is 2 weeks away, and use this warranty I paid for. This is, after all why I have it!" :grrr:
-
There are horror stories out there from licensed people, this is very true. But having the ability to report them to the DCCA is worth the money. If Joe the electrician comes to your house and causes a fire, good luck getting him to help cover the damages. At least if the person is doing work with a license you have some information about the guy ie his license number.