« Reply #20 on: August 04, 2013, 10:16:22 AM »

+1 to what kanakamaoli23 said.

I have a Fluke 77 that is almost 20 years old and it still works like a champ!

Be very careful if you remove the load center (electrical circuit breaker panel) cover to measure the voltage as the main buss bars will be exposed.  It is most likely that as kanakamaoli23 stated that the particular circuit is overloaded, but not quite enough to pop the breaker.  Possible, but highly unlikely, is that the contractor installed wiring that is not sufficient and does not meet electrical code - minimum 14 gauge for a 15 amp circuit.

Your fridge should be plugged into a dedicated circuit - check the labels in the electrical panel.  You most likely need to have some of the plugs split into separate circuits.  You can have mini-breakers (breakers that take 1/2 the physical space of a standard breaker) installed if there are no spare/open slots in the electrical panel.

Even the bathroom plugs should be a separate circuit from your other plugs in the house - with GFI plugs.  The contractor may have cut corners by combining the circuits for the plugs instead of home running separate circuits to save a couple of bucks. I.e., the bedroom plugs, bathroom plugs, living room plugs, and kitchen plugs should all have their own circuit/breaker.

I am not an electrician, but have counted wires . . .
Allright, so the fridge, water pump, and bathroom plugs I use the hair dryer on, are all on their own breakers - and the house lights dim when I use them. Can anyone explain that?  Shouldn't dim if they're on their own breaker unless like someone said, the feeder is insufficient right? I mean could be a bad breaker but THREE bad breakers for those three circuits??

ButtNutt

Re: Is there an electrician in the house?
« Reply #21 on: August 04, 2013, 10:17:31 AM »

The feeder off the pole should be fine.  If it is undersized, then the contractor should be liable for the cost for ugrading the feeder.  I have not researched it, but it most likely does not meet the building code requirements if is not sized at least at what kanakamaoli23 stated - 125A.
any way of telling if its 125a?

ButtNutt

Re: Is there an electrician in the house?
« Reply #22 on: August 04, 2013, 10:22:11 AM »

.........wiring that is not sufficient and does not meet electrical code - minimum 14 gauge for a 15 amp circuit.....
how do I tell what guage I got installed. All wires are that standard black and white looking stuff. Guage looks like what I've seen everywhere. Not thick or thin. Any way to tell?

wirecounter

Re: Is there an electrician in the house?
« Reply #23 on: August 04, 2013, 10:39:28 AM »
Allright, so the fridge, water pump, and bathroom plugs I use the hair dryer on, are all on their own breakers - and the house lights dim when I use them. Can anyone explain that?  Shouldn't dim if they're on their own breaker unless like someone said, the feeder is insufficient right? I mean could be a bad breaker but THREE bad breakers for those three circuits??

Highly unlikely, but still possible to have 3 defective breakers.  Best to check to be sure.  Seen it (unlike things happen) more often than I would think.

Not sure how to tell gauge of feeder by looking?  Kanakamaoli23?

The symptom you describe points more to an undersized (or damaged) feeder.  I would suggest calling HECO to inquire about the feeder size & describe what you are experiencing.  I seriously doubt that HECO would provide a sub-standard feeder, but I have learned never to assume anything.  If anything, try to have them schedule a technician to check it to make sure.

Don't stress too much about the dimming lights as it is only for a few minutes.  Right?  I don't think you are running the hair dryer for hours. 

Kanakamaoli23

Re: Is there an electrician in the house?
« Reply #24 on: August 04, 2013, 10:40:05 AM »
The meter main outside will have the rating on the inside of the cover. Normally the label will say 125a max load but the size of the breaker inside will be 100a breaker.

ButtNutt

Re: Is there an electrician in the house?
« Reply #25 on: August 04, 2013, 10:46:33 AM »
Thanks kanakamaoli23 and wirecounter!  I'll get the fuse for the meter and once it's working, or I get a new one, ill check out the panel.
Big mahalos!

Kanakamaoli23

Re: Is there an electrician in the house?
« Reply #26 on: August 04, 2013, 10:48:34 AM »
The wire from Heco is likely not the culprit. Heco will pull in the proper size wire depending on the size of the service the home owner chooses. Maybe the contractor ran a smaller than adequate cable from the meter main to the load center inside the home. If you have a 100a main breaker outside, the wire between the panel outside and the panel inside the house should read #2 on it.

Kanakamaoli23

Re: Is there an electrician in the house?
« Reply #27 on: August 04, 2013, 10:49:39 AM »
I really don't understand what the fuse is that you are referring to that was fried. Are you referring to a breaker? Houses don't have fuses like the way a car would.

bass monkey

Re: Is there an electrician in the house?
« Reply #28 on: August 04, 2013, 10:51:16 AM »
I really don't understand what the fuse is that you are referring to that was fried. Are you referring to a breaker? Houses don't have fuses like the way a car would.

He talking about a fuse in his multi meter.

Kanakamaoli23

Re: Is there an electrician in the house?
« Reply #29 on: August 04, 2013, 10:55:02 AM »
Ahhhh. That makes sense. Lol. I thought he was referring to something he found in his house.

Kanakamaoli23

Re: Is there an electrician in the house?
« Reply #30 on: August 04, 2013, 10:58:32 AM »
Ps I do work trade for firearms.  ;) :thumbsup:

ButtNutt

Re: Is there an electrician in the house?
« Reply #31 on: August 04, 2013, 11:13:01 AM »

The wire from Heco is likely not the culprit. Heco will pull in the proper size wire depending on the size of the service the home owner chooses. Maybe the contractor ran a smaller than adequate cable from the meter main to the load center inside the home. If you have a 100a main breaker outside, the wire between the panel outside and the panel inside the house should read #2 on it.
yeah......you heard already. The fuse in the meter. So anyway, thanks, but I don't know how I can see the wire from outside the house to the breaker panel. Maybe when I take off the cover to the panel I can tell. Is that the way you think I could see the wire? Cause from the meter outside the wire goes underground but even from the meter to the ground I can't see any wire.

Kanakamaoli23

Re: Is there an electrician in the house?
« Reply #32 on: August 04, 2013, 11:17:34 AM »
Yes you must remove the cover on the panel to see the size of the wiring.

wirecounter

Re: Is there an electrician in the house?
« Reply #33 on: August 04, 2013, 11:46:20 AM »
The wire from Heco is likely not the culprit. Heco will pull in the proper size wire depending on the size of the service the home owner chooses. Maybe the contractor ran a smaller than adequate cable from the meter main to the load center inside the home. If you have a 100a main breaker outside, the wire between the panel outside and the panel inside the house should read #2 on it.

Never thought of that, what you say makes sense.  More likely, this cable rather than the HECO feed.

So, I would suggest:

1) check the breakers.  If okay, then
2) Check the cable marker whlie you have the panel cover off.  If okay, then
3) Contact HECO.

Good luck BN!  Let us know what you discover.

ButtNutt

Re: Is there an electrician in the house?
« Reply #34 on: August 04, 2013, 03:22:04 PM »
Thanks everyone. I'm going to get a fuse now. Letter today or tomorrow I'll see what the voltage reading at the outlets are after replacing it. Then I'll go from there with taking the panel cover off or not. Fingers crossed!

Haoleb

Re: Is there an electrician in the house?
« Reply #35 on: August 04, 2013, 04:10:05 PM »
OP- Perhaps I missed something not reading word for word, but what is the actual problem you are having in the first place?

I would not be assuming you need to have a new feed wire pulled or anything of that sort just yet, and also I would highly caution against taking the cover off of your electrical panel also just yet because it does not sound like you know what you are doing (no offense)  and there are plenty of things you can accidentally touch in there that can KILL YOU

Most multimeters take a special fuse, not just something you pick up at home depot. When it says replace only with such and such a fuse please heed that warning. I can tell you from experience. I was doing a startup at a water remediation plant, inside of the main pump station panel we had built which is supplied by 3 phase 480v 200amp serivice. I was testing all sorts of items and had not remembered my meter leads were still set for measuring current when I was testing 4-20ma devices... Most good meters will beep at you when you turn the knob to voltage and the leads are not connected properly.. this one did not...  well.. I went to take a voltage measurement on one of the pump station breakers and in an instant there was a good few sparks, and a gunshot sound that was my multimeter literally exploding. It was a good thing I was not holding the meter. Also good that I had a spare meter with me. A while back I had replaced a blown fuse in it with a generic one, not the 10 dollar fluke one... Lesson learned.

Also, when you do take voltage measurements, Measure from hot to neutral (hot is the smaller blade) this should read around 120v
Measure from hot to ground. also should read around 120v
Measure from neutral to ground. should read 0v or close to thereabouts.

If your meter has a recording function you can turn that on and see how much voltage sag you are getting when heavy loads are turned on if that is the problem you are having.

bass monkey

Re: Is there an electrician in the house?
« Reply #36 on: August 04, 2013, 04:23:24 PM »
OP- Perhaps I missed something not reading word for word, but what is the actual problem you are having in the first place?

I would not be assuming you need to have a new feed wire pulled or anything of that sort just yet, and also I would highly caution against taking the cover off of your electrical panel also just yet because it does not sound like you know what you are doing (no offense)  and there are plenty of things you can accidentally touch in there that can KILL YOU

Most multimeters take a special fuse, not just something you pick up at home depot. When it says replace only with such and such a fuse please heed that warning. I can tell you from experience. I was doing a startup at a water remediation plant, inside of the main pump station panel we had built which is supplied by 3 phase 480v 200amp serivice. I was testing all sorts of items and had not remembered my meter leads were still set for measuring current when I was testing 4-20ma devices... Most good meters will beep at you when you turn the knob to voltage and the leads are not connected properly.. this one did not...  well.. I went to take a voltage measurement on one of the pump station breakers and in an instant there was a good few sparks, and a gunshot sound that was my multimeter literally exploding. It was a good thing I was not holding the meter. Also good that I had a spare meter with me. A while back I had replaced a blown fuse in it with a generic one, not the 10 dollar fluke one... Lesson learned.

Also, when you do take voltage measurements, Measure from hot to neutral (hot is the smaller blade) this should read around 120v
Measure from hot to ground. also should read around 120v
Measure from neutral to ground. should read 0v or close to thereabouts.

If your meter has a recording function you can turn that on and see how much voltage sag you are getting when heavy loads are turned on if that is the problem you are having.


Problem started here.  So it kinda turned into a issue of his meter is blown or house wiring sucks.

I got an ETek multimeter and every outlet in my home tests about 6.4V. Is that possible?  I got it long ago so I can't return it, but before I go spend 50$ on a new one I figured I'd ask if that's possible appliances seem to work fine but when my catchment pump or fridge or hair dryer go on the house lights dim?  Is it possible the 6V is real or do I have a bad multimeter?

Haoleb

Re: Is there an electrician in the house?
« Reply #37 on: August 04, 2013, 04:47:23 PM »
Yeah, I did see that part but obviously something caused him to check the voltage in the first place. Clearly the actual voltage is not 6.4vac as nothing will run from that. It is however possible to measure such a voltage if the breakers were all turned off when he was taking these readings as there will be some voltage potential between ground and the de-energized circuit.

OP- If the problem is the lights dimming, are they just dimming for a second or it is a constant thing?

All of those loads you listed will present a heavy current draw and even in a modern house with sufficient wiring you will likely still see dimming especially when they are initially turned on. You should not really notice a significant and constant dimming of your house lights the entire time though.
« Last Edit: August 04, 2013, 04:54:55 PM by Haoleb »

ButtNutt

Re: Is there an electrician in the house?
« Reply #38 on: August 04, 2013, 08:19:30 PM »

OP- Perhaps I missed something not reading word for word, but what is the actual problem you are having in the first place?

I would not be assuming you need to have a new feed wire pulled or anything of that sort just yet, and also I would highly caution against taking the cover off of your electrical panel also just yet because it does not sound like you know what you are doing (no offense)  and there are plenty of things you can accidentally touch in there that can KILL YOU

Most multimeters take a special fuse, not just something you pick up at home depot. When it says replace only with such and such a fuse please heed that warning. I can tell you from experience. I was doing a startup at a water remediation plant, inside of the main pump station panel we had built which is supplied by 3 phase 480v 200amp serivice. I was testing all sorts of items and had not remembered my meter leads were still set for measuring current when I was testing 4-20ma devices... Most good meters will beep at you when you turn the knob to voltage and the leads are not connected properly.. this one did not...  well.. I went to take a voltage measurement on one of the pump station breakers and in an instant there was a good few sparks, and a gunshot sound that was my multimeter literally exploding. It was a good thing I was not holding the meter. Also good that I had a spare meter with me. A while back I had replaced a blown fuse in it with a generic one, not the 10 dollar fluke one... Lesson learned.

Also, when you do take voltage measurements, Measure from hot to neutral (hot is the smaller blade) this should read around 120v
Measure from hot to ground. also should read around 120v
Measure from neutral to ground. should read 0v or close to thereabouts.

If your meter has a recording function you can turn that on and see how much voltage sag you are getting when heavy loads are turned on if that is the problem you are having.
Hey thanks for the warnings and advice. Funny thing is that this post makes me seem like a total noob but I've replaced a 50A breaker for my range, replaced the thermostat and elements in my water heater, and installed lighting in my kitchen and bathroom, so im not totally green, but know my limits and when to call a professional. Thing is when i did all that, it was during the first year here and i was using my friends multimeter before he moved.  so the multimeter I originally bought sat in my tool bag and never got used till now.  So anyways,  the next poster after you postulated a logical assumption which was that something must have started this whole thing, and that is true. I just got home with the fuse so ill post in a few minutes what I get and I'll give the history as well, cause that will probably help you guys help me. 















ButtNutt

Re: Is there an electrician in the house?
« Reply #39 on: August 04, 2013, 08:31:03 PM »
Btw thanks to RN230 for tactfully PM'ing and figuring out I must have blown the fuse in the multi by using it incorrectly :0